Before you connect the driver interface to the
sat-nms ACU2-19V2, take care the mains of
drive cabinet is switched off and ACU2-19V2 is in STOP
condition before connecting the drive cabinet.
- Click the STOP button on the
sat-nms ACU2-19V2`s website. By this you can
be sure that no motor movement will occur connecting the drive
cabinet.
- Connect the drive interface to the sat-nms
ACU2-19V2 as described in chapter 4.2.2 .
- Click the RESET button on the
sat-nms ACU2-19V2`s website.
- Check the motor rotating directions, if necessary change it by
interchanging the two wire of the motor cable. We recommend not to move
all three axes at the same time, do it step-by-step
- Drive the antenna in every direction (AZ, EL and POL) until the
limit switches stop the motor movement to ensure that the limit switches
work well. ATTENTION! While doing this test it is
absolutely necessary to be very mindful to check, if nothing
collides!
- Set the soft-limits to the desired values (e.g. 1 degree before the
hardware limit switch is activated)
- Now the new antenna controller is operational and you can move all
three axes.