The angle encoders have to be connected directly to the core module of the sat-nms ACU2-ODU, which is called sat-nms ACU2-ODM. Inside, the sat-nms ACU2-ODM consists of a main board and two or three interface boards with the circuitry for the position sensors. These boards are different for each type of position sensor.

It is essential, that the shield of the encoder cable is connected to ground with low impedance at the cabinet, but not at antenna side (isolate the shield well to ensure that shield is not connected to antenna ground!). Also take care that the unshielded part of the cable is as short as possible. To ensure proper ground connection in the cabinet, there are two possibilities:

  1. connect the shield to the PE terminals right below sat-nms ACU2-ODM. Take care, that the shield cable is as short as possible. You can see this on the following picture. Encoder-connection.gif

  2. there are three brackets that can be used to ground connect the shield extensive. You have to remove the outer insulation of the cable in the area of this bracket. Take care, that shielding is not damaged during removing of isolation. Feed the cable through the bracket ad close it by considering, that the de-insulated part fits the bracket. If you decide to go with 1), you can nevertheless use this bracket as strain-relief for the cables.

Actually interfaces for three types of position encoders are available with the sat-nms ACU:

Below the pinout of a resolver type interface board is shown. The ACU is available with resolver, SSI or analog position sensor interfaces. You have to select type of interface when you order the ACU.

pin signal description type
1 GND
2 SIN resolver SIN IN
3 GND resolver SIN IN
4 COS resolver COS IN
5 GND resolver COS IN
6 REF drive signal to resolver OUT
7 GND drive signal to resolver OUT
8 GND

The ACU resolver interface is designed for resolvers with an impedance of 100 Ohms or more and transfer factor 0.5. The interface applies 4Veff / 2000Hz to the resolver drive coil. It expects 2Veff at the sine / cosine inputs at the maximum positions.

resolv.gif

When connecting a resolver to the ACU, please consider the following:

CON18, CON19, CON20 SSI Positional Encoder Interface

Below the pinout of a SSI type positional encoder interface board is shown. The ACU is available with resolver, SSI or analog position sensor interfaces. You have to select type of interface when you order the ACU.

The SSI positional encoder may be powered from the ACU internal power supply. +5V and +24V clamps are provided at the connector. To avoid ground loops, the cable shield should be connected either to pin 1 at the ACU or to the ground at the encoder housing, never at both ends.

pin signal description type
1 GND
2 SSI-Data+ SSI data IN
3 SSI-Data- SSI data IN
4 SSI CLK+ SSI clock OUT
5 SSI CLK- SSI clock OUT
6
7 +5V encoder power supply
8 +24V encoder power supply

CON18, CON19, CON20 Analog Angle Sensor Interface

Below the pinout of an analog type positional sensor interface board is shown. The ACU is available with resolver, SSI or analog position sensor interfaces. You have to select type of interface when you order the ACU.

pin signal description type
1 AGND analog ground OUT
2 INPUT A/D converter input IN
3 REF reference voltage OUT
4 AGND analog ground OUT
5 +15V (opt) optional DC out OUT
6 -15V (opt) optional DC out OUT
7 +9V (opt) optional DC out OUT
8 GND digital ground OUT