4.6.11 Modbus Temperature Sensors Setup Registers

Temperature sensor setup registers start at register 6001, each sensor covers 30 registers for its setup data. This means that temperature sensor 2 starts at register 06031, temperature sensor 3 at 06061 and so on.

Temperature sensor 1 measures the board temperature, sensors 2..5 may be connected to external PT1000 sensors. Sensor 1 therefore is limited to temperature monitoring, no closed loop temperature control may be defined for this sensor. Beside this, the name of this sensor is fixed to 'board temperature'.

The register definitions for sensor 1 are:

  Register    Purpose               Remarks
  
  06001       sensor 1 enable       1 = show readings, check limits
  06002       sensor 1 name         always reads 'board temperature'
  06017       sensor 1 cal. offset
  06018       sensor 1 low limit    
  06019       sensor 1 high limits

  The register definitions for sensor 2 are:

  Register    Purpose               Remarks
  
  06031       sensor 2 enable       1 = show readings, check limits
  06032       sensor 2 name         up to 29 characters + 
                                    0-termination in 15 registers
  06047       sendor 2 cal. offset
  06048       sensor 2 low limit        
  06049       sensor 2 high limits
  06050       sensor 2 control loop 0 = no control loop
              mode                  1 = heating
                                    2 = cooling
  06051       control loop output   0..15 referring to output 
                                    number 1..16. the referenced 
                                    output must be configured as 
                                    TCTRL_OUTPUT
  06052       control loop inhibit  input number 0..47 or -1 to
              input                 to select no input
  06053       target temperature
  06054       hysteresis

All temperature values are signed integers scaled to 1/10 centigrades. Temperature control loop parameters only are available if this feature is licensed.