Temperature sensor setup registers start at register 6001, each sensor covers 30 registers for its setup data. This means that temperature sensor 2 starts at register 06031, temperature sensor 3 at 06061 and so on.
Temperature sensor 1 measures the board temperature, sensors 2..5 may be connected to external PT1000 sensors. Sensor 1 therefore is limited to temperature monitoring, no closed loop temperature control may be defined for this sensor. Beside this, the name of this sensor is fixed to 'board temperature'.
The register definitions for sensor 1 are:
Register Purpose Remarks
06001 sensor 1 enable 1 = show readings, check limits
06002 sensor 1 name always reads 'board temperature'
06017 sensor 1 cal. offset
06018 sensor 1 low limit
06019 sensor 1 high limits
The register definitions for sensor 2 are:
Register Purpose Remarks
06031 sensor 2 enable 1 = show readings, check limits
06032 sensor 2 name up to 29 characters +
0-termination in 15 registers
06047 sendor 2 cal. offset
06048 sensor 2 low limit
06049 sensor 2 high limits
06050 sensor 2 control loop 0 = no control loop
mode 1 = heating
2 = cooling
06051 control loop output 0..15 referring to output
number 1..16. the referenced
output must be configured as
TCTRL_OUTPUT
06052 control loop inhibit input number 0..47 or -1 to
input to select no input
06053 target temperature
06054 hysteresis
All temperature values are signed integers scaled to 1/10 centigrades. Temperature control loop parameters only are available if this feature is licensed.