4.3 Parameter list

The table below shows the complete list of M&C parameters the power sensor knows. For each parameter the data type and a short description is given.

name type unit description
dbms r/o float dBm The calibrated / temperature compensated power reading in dBm. See chapter Power Reading power reading for a detailed description.
adcv r/o int The raw ADC value without any calibration or compensation applied. The value is in the range 0 .. 65535.
temp r/o float °C The temperature measured inside the power sensor enclosure. The value is in degree Celsius.
sens r/o LOW HIGH The actual input amplifier sensivity. sens is either HIGH or LOW
tflt r/o FAULT OK The threshold fault state. if the power reading is below the threshold the value is FAULT else OK
tsya r/o NTP time sync alarm
smod AUTO LOW HIGH Sets the sensivity range, the power sensor uses. See chapter Operational Settings Sensor Sensitivity for a detailed description.
fltr OFF FAST SLOW Sets the filter, the power sensor applies to the measured values. See chapter Operational Settings Average Filter for a detailed description.
thrh float dBm Defines the alarm threshold value. See chapter Operational Settings Alarm threshold for a detailed description.
freq int MHz Defines the frequency of the measured signal in MHz. See chapter Operational Settings RF frequency for a detailed description.
fcor r/o float dB The calibration offset, the power sensor actually adds to each measured value due to the frequency response calibration. See chapter Power Reading cal offest freq for a detailed description.
offs float dB The value [dB] specified with this parameter is added to the measured power before it is displayed and compared to the fault threshold value. See chapter Operational Settings Display Offset for a detailed description.
srno r/o character string The power sensor's serial number. This is a five digit hexadecimal number which uniquely identifies each individual unit. For the one line command use ' snr' instead 'srno'.
note character string The Power Sensor Note / comment, which is displayed by the power sensor as the heading of the 'Readings' page.
udpa character string UDP destination address
sver r/o character string Software version
scon character string SNMP system contact
snam character string SNMP system name
sloc character string SNMP system location
rcom character string SNMP read community
wcom character string SNMP write community
tcom character string SNMP trap community
autr DISABLED,ENABLED SNMP traps enabled, disabled
ipt1..4 character string SNMP Trap destination address
stim character string Set the actual time in the following format
'yyyy-mm-dd hh:mm:ss'
time r/o character string Get the actual time in the following format
'yyyy-mm-dd hh:mm:ss'
lsyn r/o character string Last time synchronization
ntp1..2 character string NTP server IP address
ivpr r/o character string Invalid parameter value, set only if the entered value out of range